Previous Page | Next Page Contents Glossary Index Preparing the Physical Environment > Physical Requirements >

Power

Ensure that you have an electrical outlet that supports 12 kVA and meets the power requirements listed in Table 11 for each printer. This outlet must supply 3-phase power and be able to disconnect power from each printer, such as:

Table 11. Electrical Requirements
Country AC Voltages Wiring Information Phase Circuit Rating
Nominal Minimum Maximum
U.S. Canada
60 Hz/208
60 Hz/220
60 Hz/230
60 Hz/240
60 Hz/187
60 Hz/198
60 Hz/207
60 Hz/216
60 Hz/229
60 Hz/242
60 Hz/252
60 Hz/264
4-wire power cable with three phases and ground. Neutral is not required. 3 60 Amperes
Japan
50 Hz/200
60 Hz/200
50 Hz/180
60 Hz/180
50 Hz/220
60 Hz/220
4-wire power cable with three phases and ground. Neutral is not required. 3 60 Amperes
Europe
50 Hz/380
50 Hz/400
50 Hz/415
50 Hz/342
50 Hz/360
50 Hz/374
50 Hz/418
50 Hz/440
50 Hz/456
5-wire power cable with three phases, ground, and neutral. Direct connection of neutral to ground required. 3 25 Amperes
Attention: The 50-Hz 380/400/415 Volt version does not support non-earthed neutral and impedance-grounded neutral power distribution systems. Installation on an impedance-grounded neutral power system (IT Power System) could result in failures of motors and transformers in the printer.